Electric wiring and bulb types for coop.

Discussion in 'Coop & Run - Design, Construction, & Maintenance' started by Tinworm, Nov 18, 2012.

  1. Tinworm

    Tinworm New Egg

    8
    0
    9
    Nov 18, 2012
    Is 10/2 enough to handle 1 heat lamp and 1 LED light at 100' ?Heat lamp will be on thermostat. Not sure of light types on wire.LED vs cfl vs standard bulbs, any suggestions?
     
  2. KDK1

    KDK1 Chillin' With My Peeps

    817
    32
    144
    Jun 29, 2011
    Tennessee Plateau
    10/2 w/ground is big enough to handle 30 amps. Plenty big enough to run a heat lamp and whatever light you choose... incandescent, halogen, LED, CFL. Anything you want.
     
    1 person likes this.
  3. Tinworm

    Tinworm New Egg

    8
    0
    9
    Nov 18, 2012
    Ok, thanks for the info KDK1.
     