Being that I'm still in the process of building a winter coop, yes I've been slacking, adequate ventilation has been on my mind. So I decided to do some research this morning. After a few hours of sifting through university publications and the like I pulled out the info that is pertinent to us BYC'ers.
Chickens need 0.5 cfm air flow. A handy formula for gable and eave vent requirements is A=4.7Q/V. Your slope of roof should be between 4/12 and 6/12 (edit: took out the angles I'd figured in my head that were off. Pitch is correct still) to ensure proper mixing of fresh air and coop air.
Q= required air flow = # of chickens x 0.5cfm
V= wind speed
A= your minimum required square inch of opening in gable/ridge vent and that amount again in each sofit vent.
This formula works for each 10 feet of building width. As we are BYC'ers I doubt we have buildings wider than 10ft but if so than double the area for up to 20 feet, etc.
You can Google your state/region for average wind speed. Here in New England the average is 8 miles/hour in winter and 5 mph in summer. The lowest wind speed is your parameter for area needed.
Example:
I have 7 chickens. My coop is less than 10ft wide (gable side). My lowest average wind speed is 5 mph.
A= 4.7 (7 x 0.5)/ 5 = 3.29 square inches. Voila! my gable vents need to add up to a minimum of 3.29 and each eave vent the same.
I'd already drilled a pattern of 1/2 inch holes in the gable, 7 holes each side. Using the area of a circle...
(.5/2)^2 (3.14)14 holes = 2.75 square inches. Not enough!
If I re-drill the holes to 5/8 inch then: [(5/8)/2]^2 (3.14)14= 4.29 square inches. More than adequate.
Therefore I'll be drilling 7 holes with 5/8 drill each gable end and 14 holes under both eave ends.
I hope this wasn't confusing and is helpful.
You may think 0.5cfm is not a lot but a chicken is small, 10cfm is required for a hog and 35cfm for beef cattle. To circulate out the moisture and gases caused by one chicken doesn't require much and this is a easy way to ensure the minimum
Chickens need 0.5 cfm air flow. A handy formula for gable and eave vent requirements is A=4.7Q/V. Your slope of roof should be between 4/12 and 6/12 (edit: took out the angles I'd figured in my head that were off. Pitch is correct still) to ensure proper mixing of fresh air and coop air.
Q= required air flow = # of chickens x 0.5cfm
V= wind speed
A= your minimum required square inch of opening in gable/ridge vent and that amount again in each sofit vent.
This formula works for each 10 feet of building width. As we are BYC'ers I doubt we have buildings wider than 10ft but if so than double the area for up to 20 feet, etc.
You can Google your state/region for average wind speed. Here in New England the average is 8 miles/hour in winter and 5 mph in summer. The lowest wind speed is your parameter for area needed.
Example:
I have 7 chickens. My coop is less than 10ft wide (gable side). My lowest average wind speed is 5 mph.
A= 4.7 (7 x 0.5)/ 5 = 3.29 square inches. Voila! my gable vents need to add up to a minimum of 3.29 and each eave vent the same.
I'd already drilled a pattern of 1/2 inch holes in the gable, 7 holes each side. Using the area of a circle...
(.5/2)^2 (3.14)14 holes = 2.75 square inches. Not enough!
If I re-drill the holes to 5/8 inch then: [(5/8)/2]^2 (3.14)14= 4.29 square inches. More than adequate.
Therefore I'll be drilling 7 holes with 5/8 drill each gable end and 14 holes under both eave ends.
I hope this wasn't confusing and is helpful.
You may think 0.5cfm is not a lot but a chicken is small, 10cfm is required for a hog and 35cfm for beef cattle. To circulate out the moisture and gases caused by one chicken doesn't require much and this is a easy way to ensure the minimum